It could only happen to us Boiler has shut down E110 I think

<< < (19/23) > >>

McCabe-Thiele (Ted):

--- Quote from: royhall on January 15, 2025, 08:26:39 AM ---Your lucky. Some of the fires are attached to the boiler. The flue gases usually go up the centre tube with air drawn in around it via the outer pipe. It's safer that way , if the flue pipe leaks it goes into the incoming air instead of possibly into the room. It can also be detected by flue gas analysis. Some have two separate pipes. They were a horrible thing to fit

Sent from my Pixel 7 Pro using Tapatalk

--- End quote ---

That makes sense for safety.

The plumber who installed the BBU HE did not use the front fire to rear boiler cable wire attachment system.
He used a wide velcro on the fire & hearth, it sounded a bodge at the time but works well, you can remove the front fire & move it away from the boiler without having to disconnect the power cable.

My original Baxi Bermuda back boiler/gas fire was like that, not condensing so it was super reliable. It never broke down in over 25 years , I replaced it when it started kettling quite badly, not as efficient as the later condensing type. The original central heating was installed by the builder, it was a Baxi Bermuda Back boiler with a wooden surround to the gas fire front. That boiler lasted from 1968 to 1987, replaced due to a corroded heat exchanger for a modern version of the same boiler/gas fire front  that lasted from 1987 to 2014. At the time I could afford the new boiler but not to convert from Primatic to a fully pumped system, had I done so it would probably have lasted even longer.

Photo to show the end finish that the wife loves.

.PXL_20250115_095834396 by Macabe Thiele, on Flickr


This is the boiler behind the electric fire with the front cover off, the condensate tank has been removed, hence the gap lower left,revealing how corrosive the water is as it has overflowed into the base of the boiler..


PXL_20240129_144855822 by Macabe Thiele, on Flickr

royhall:
That corrosion is nearly always there on those boilers. Condensate is always slightly acidic, which when it spills, will corrode the steel rapidly.

Sent from my Pixel 7 Pro using Tapatalk

McCabe-Thiele (Ted):
Thanks for that Roy, here is the old condensate tank that was replaced in January 2024.

.condensate tank by Macabe Thiele, on Flickr

royhall:
Blimey that's full of corrosion particles no wonder it's packed in. Something inside your boiler is rotting away and it's been washed out by the condensate. When's the last time the burner was stripped out.

Sent from my Pixel 7 Pro using Tapatalk

McCabe-Thiele (Ted):

--- Quote from: royhall on January 15, 2025, 12:29:01 PM ---Blimey that's full of corrosion particles no wonder it's packed in. Something inside your boiler is rotting away and it's been washed out by the condensate. When's the last time the burner was stripped out.

Sent from my Pixel 7 Pro using Tapatalk

--- End quote ---

It's been serviced by a Baxi Engineer for the last 6 years, he takes about 45-60  mins to carry out the service, I've never watched him. I have no idea if he stripped out the burner, he fitted a complete heat exchanger in Jan 2024.

My original installer who did the previous services was in & out in under 15 mins, he just plugged in his laptop and printed off  some gas readings for O2,CO & CO2.